Pat,

Attached are drawings for the CG2 computer room and FL2-3095 showing the 
maximum rack weights. 

Building floor load ratings given in lbs/sqft are for distributed loads, 
a common number is 75- 100 lbs/sq ft.  When an item exceeds the floor 
load rating (such as a computer rack) structural engineers have been 
called in to assign specific weight limits based on location in the room 
and other surrounding weights.

Hope this helps,
Steven